Question
How will you calibrate an absolute pressure transmitter vaccum manometer Range 0-400mm abs ?

Answers

The procedure for calibration is as follows :
1. Connect air supply to the transmitter.
2. Connect a test gauge of 0-1.4 Kg/cm2 to the output.
3. Connect Vaccum pump with tee off to the manometter.
4. Apply 760 mm Vaccum ( or Hearest ) and adjust zero.
5. Apply 360 mm Vaccum adjust span. ( 760 - 360 = 400 mm abs. )   Your Comment






Search
Can you Answer!!
  • Q What kind of a person are you - Introvert/Extrovert
  • Q When and who founded jquery ?
  • Q How to Pass values between pages?
  • Q What are the constants defined by both Flaot and Double classes?
  • Q Why do you want to work for us? What can you offer us that other students can't?
  • Q What is the closeness function?
  • Q How can I see a GP if I'm away from home?
  • Q Design and describe a system/application that will most efficiently produce a report of the top 1 million Google search requests. These are the particulars: 1) You are given 12 servers to work with. They are all dual-processor machines with 4Gb of RAM, 4x400GB hard drives and networked together.(Basically, nothing more than high-end PC’s) 2) The log data has already been cleaned for you. It consists of 100 Billion log lines, broken down into 12 320 GB files of 40-byte search terms per line. 3) You can use only custom written applications or available free open-source software.
  • Q Some kinds of material; for example, certain fluids are not suited to interim storage in a goods receipt area. They are taken directly to the destination storage bin when they arrive (for example, in a road tanker). In this case, the goods receipt posting in the inventory management should not trigger the creation of transfer requirement. How can we set this?
  • Q What do you do when priorities change quickly?
  • Q Why do we need lungs?